Re: Bonding Conduit At Utility Pole
Highvoltage, I didn't mean to ruffle your feathers and no insult was intended. Obviously, I did insult you and for that I apologize.
You are correct, I have never been a lineman but I have written or checked work orders for the line department for 35 years. I have a bit more than a passing knowledge of the NESC so lets go through your litany.
Most modern primary and neutral conductors are aluminum except for the wire that goes from the stirrups to the cutouts, lightning arresters, primary bushings, etc. For the current the phase and neutrals normally carry, they are way oversized in most cases. The sizes we use are for the physical strength and not for ampacity. This changes on the secondary side of the transformer where ampacity is the major consideration.
The pole down grounds are required by the NESC to be #6 Cu. and some electric utilities will oversize the pole ground. We use #6 and will use #4 on transmission poles for the static down ground. Some electric utilities have started using a larger size copperweld down ground but I don't know how large it is. Copperweld is a steel wire with a copper welded on the outside of the steel and is no different than a copperweld ground rod. This keeps thieves away from the ground wire.
The importance of grounding to a #4 for a 200 ampere service is to be able to carry the fault current if there is a ground fault in the conduit. The physics are the same whether the ground fault is in the service conduit on the side of a home or on a pole. You have to go to 250.66 to size your grounding jumper and if it is attached to a #6, why bother using the #4 from the table? If it a 400 ampere service, now you are talking about 1/0 and that #6 will be way too small.
If you are building a riser, you could be using a ? X 8" listed Copperweld rod and #6 Cu. running to it (that also is acceptable in the NESC).
I agree with you about the transformer configurations.
I hope we can disagree with each other without getting mad. As I said before, I had no intention of insulting you.