bedrooms
Today, the inspectior failed me because I have two (2) arc fault breakes suppling three (3) bedrooms. According the 1999 nec 210-12 (b), there is nothing that states this can not happen? Unless there is something else that indicates otherwise is this acceptable. Responce ASAP
thank you
roger
Fl
Retired Electrician
Re: bedrooms
Tony, you are absolutly right, there is nothing wrong with this installation as far as the NEC is concerned.
What is the inspector specificaly citing as the violation?
Roger
[ February 25, 2004, 09:22 PM: Message edited by: roger ]
tonyi
Re: bedrooms
That scenario is common as dirt.
Is there some other factor here, like these being huge BR's and the branches being 15A where you might be bonked an a VA-ft issue?
jimwalker
TAMPA FLORIDA
Re: bedrooms
You could probably put all 3 or 4 bed rooms one 1 circuit.The way i see it is 600 sq feet on a 15 amp afci.I dont suggest it,but legal.With the number of problems afci are causing i would prefer 1 to a bedroom or at a min.run seperate HR from each and join them at panel,at least make isolating problem easy.
joek
Re: bedrooms
210.12(B) covers all outlets in bedrooms. This includes lighting and receptacle outlets. Did you AFCI the lighting outlets?
roger
Fl
Retired Electrician
Re: bedrooms
Joe,
not so in the 99 code cycle.
The 99 code only required circuits supplying "receptacle" outlets to be AFCI protected.
Roger