Why an auto transformer always has a tertiary winding & that is of delta connection?:?
D Debabrata Member Location Kolkata Jun 3, 2015 #1 Why an auto transformer always has a tertiary winding & that is of delta connection?:?
T templdl Senior Member Location Wisconsin Jun 3, 2015 #2 Debabrata said: Why an auto transformer always has a tertiary winding & that is of delta connection?:? Click to expand... By "always", Auto transformer as is a motor starter or as in a buck/boost transformer?
Debabrata said: Why an auto transformer always has a tertiary winding & that is of delta connection?:? Click to expand... By "always", Auto transformer as is a motor starter or as in a buck/boost transformer?
Tony S Senior Member Location Resting under the Major Oak UK Jun 3, 2015 #3 An autotransformer is almost transparent to harmonics and the fault currents pretty horrendous, the tertiary winding is to control both. For a motor starter I wouldn?t expect to see one, for the time it?s in circuit it?s not worth the expense.