Re: Article 90
ATT is one of the few wireless carriers that is exempt from code and considered a utility. Cingular is owned and operated by SBC, so I assume they are exempt. However, it is on a local by local basis, and if they are in a multi-tenant building not under their exclusive control like a high-rise, they will not be exempt.
Most of the wireless sites are built with pre-fabricated buildings constructed in a factory with all the equipment installed. IMO the code does address DC and RF systems used in wireless and telecom. IMO the wireless practices exceed/meet NEC. For example, the 24-volt DC systems are not required to be grounded, but you will find them grounded. The DC circuit and ground conductors are larger than required by table 310.16, and table 250.122. The only gray area I know of is with the batteries. We do not use fuses between the battery and charge buss, only if required by AHJ if they are involved and can catch it.
The coax sheath is bonded multiple times to the tower and where it leaves the tower. Once the coax enters the building it is connected to an entrance bulkhead with ADU?s. The bulkhead is a copper plate that extends all the way down to the ground ring or a copper plate with multiple conductors going down to the ground ring.
Grounding is another area that great care and extremes are taken. Most designs require a 5-ohm or less. This is accomplished by using a ground rings around the building, fence line, and around the tower. The tower and building foundations employ a Ufer ground. The rings will often use radials that extend out to the guy wires if employed. If soil conditions are poor we will use several chemical rods with the rings and radials to enhance the system. The GES is then brought into the building via the cable entrance bulkhead and used a single point reference for all the TVSS, ADU?s, AC service entrance, DC power supply, halo ground, and equipment frame grounds. IMO this meets any code requirement. Some may not go to this extent, but most do.