I am involved in the design of PLC control panels. After hours of paging back and forth, I think I am getting the gist of NEC Article 725. Here is how I understand it in a somewhat simplified and abbreviated way. Please feel free to critique my understanding if I got it wrong.
If you use 16 AWG or 18 AWG conductors, Article 725 applies. If the wire insulation is rated 600 Volts you can use Class 1 wiring methods. Class 1 circuits can be run with power circuits in a factory or field assembled control center. (PLC panel?)
If the insulation is rated 300 Volts, that is typical of analog cabling, you must use Class 2 or 3 wiring methods. If you use Class 2 or 3, you must use a Class 2 or 3, Listed, power supply. Class 2 and 3 circuits must be separated from Class 1 and power circuits.
What I don?t understand is, if you have 300 Volt rated cable but have a proprietary, non-listed power supply designed for the PLC, is the installation not permitted?