As per this article, am I required to install a grounded conductor when installing/replacing a occupancy sensor in a existing wall switch location?
Lutron has OS's that state no neutral required.
RC
If it is a new switch, I agree, but this thread is about replacing a snap switch with an occupancy sensor. In my opinion, the code does not require running a grounded conductor to the switch box unless the new occupancy sensor requires a grounded conductor.You still need a neutral at that switch under the 2011.
If it is a new switch, I agree, but this thread is about replacing a snap switch with an occupancy sensor. In my opinion, the code does not require running a grounded conductor to the switch box unless the new occupancy sensor requires a grounded conductor.
I agree.I would agree with that but if the occupancy sensor requires a neutral you have no choice
I think it will be a few years. I don't think UL has even issued the new standard.I wonder how long the older style will be around?