AL Feeders

Status
Not open for further replies.

ashtrak

Senior Member
Location
Maryland
Can anyone see a problem with using Al feeders instead of copper. I've got a 600 amp three phase service and the owner would like me to investigate that option for cost savings.I'd be replacing 4#250's and a ground for a sub pnl feed, and replaceing the main feeder (2 sets of 4-#350and gnd). All branch ckts would remain Cu. POCO is coming in with one set #500. Other than the obvious proper torquing at terminations is it still necessary to penatrox the terminations? Thanks
 

bphgravity

Senior Member
Location
Florida
Aluminum conductors are just fine. You only need to use anti-oxidant compound to the terminations if it is called for in the instructions for the equipment or terminal manufacturer.
 