Abandoned service to building

Status
Not open for further replies.

billp2223

Member
A building has been demolished, that has a buried power service form the local power companies transformer. One end of this line is still hooked and energized at the transformer the other end is buried and taped up. Is there any requirements in the NEC code that states that this service should be disconnected at the transformer?
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: Abandoned service to building

No. You say it's taped up. Where? Is it in a vault at the property line? If it's protected it's probably OK but if it's accessable it should be disconnected. I would have the owner get in touch with the POCO. He could even mention a theft of service viewpoint.

-Hal
 