The 2008 NEC had a code section (690.47[D]) for additional electrodes for array grounding. In the 2011 NEC, this section was elimated. My understanding is it is now back in the 2014 edition of NEC. (Sorry, I do not have a copy of the '14 NEC, as we just went to the '11 edition 5 months ago.)

Anyone have anything concerning this? Was this a mistaken ommision, or intentional and then brought back? I have not found anything from NFPA addressing this, so I am seeking information. Some jurisdictions are enforcing this, interpreting this was a mistake. Others are not enforcing it, as it is not in the '11 code and therfore cannot be enforced.

Any help is appreciated.

Mike
 

inspector23

Senior Member
Location
Temecula, CA
Thank you

Thank you

Thank you for that link from Mike Holt. It is clear, consice, and definitely worth the time investment of reviewing it. For once I am glad California is a whole code cycle behind. Gives us a valid reason not enforce it when it comes back into the code in the 2015 California Electrical Code [2014 NEC].

Thanks for your time and input. It really has helped guide our jurisdiction in how we will be interpreting this omisson for this code cycle and how we will address it in the next California code cycle.

Mike
 

c_picard

Senior Member
Location
USA
Help spread the word. I'd love to see this disappear again in 2017.

It has no foundation based on safety or logic. How many rooftop HVAC units are out there happily humming along with a properly sized EGC?

'nuff said.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
It is back in the 2014 NEC, albeit in a slightly different form.

I think there is disagreement about whether it was taken out by mistake or not, but I don't know the full story. Hopefully someone else can fill that in, I've been curious myself.

There's also this:
http://forums.mikeholt.com/showthread.php?t=158154
Can someone summarize it? My company blocks access to youtube on its network.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Can someone summarize it? My company blocks access to youtube on its network.

Mike says it's dangerous in case of a nearby lightning strike to have grounding electrodes at widely removed locations inside a building tied together by a bonding jumper or other metal parts that run through the building. A lightning strike causes a voltage gradient through the ground that will result in destructive current flowing along those metal parts. In his opinion, the grounding electrode system should tie all grounded electrical parts and equipment in a building to ground through a single point.

Seems to me that video implicitly calls into question 690.47(C)(1) as well as 690.47(D). I've seen similar criticisms on other forums.
 

SolarPro

Senior Member
Location
Austin, TX
From a recent SolarPro magazine article on NEC 2014:

?D? is for danger? The requirements found in Section 690.47(D) have been controversial since they were first added to the Code in 2008. (See ?Additional Electrodes for Array Grounding,? SolarPro magazine, October/November 2008.) Some industry stakeholders pointed out that the requirements did little to improve system safety and they significantly increased costs, especially on smaller PV systems. Others complained that the section was poorly written, included language ripe for misinterpretation and contained requirements that were difficult to enforce or comply with. As a result, many industry veterans were pleased when this language was removed from NEC 2011. Unfortunately for them, Section 690.47(D) reappears in NEC 2014, only with a twist this time?a one-word change that has inspired a new set of detractors.

Whereas the 2008 version of Section 690.47(D) required ?additional electrodes for array grounding,? the 2014 version requires ?additional auxiliary electrodes for array grounding.? According to a substantiation in the ROC, the intent of adding the term auxiliary was to signal that ?this grounding electrode is not required to be tied into the premises? grounding-electrode system; and if multiple grounding electrodes are installed, they do not need to be bonded together by a dedicated bonding conductor.? The substantiation concludes by noting that the dc EGC ?will serve to bond the electrodes in the PV array together. A separate bonding conductor would be duplicative.?

Not everyone agrees with this assessment. Mike Holt, the founder of Mike Holt Enterprises, is a Code expert and electrical training specialist. According to a 26-minute YouTube video presentation (see Resources), Holt?s opinion is that ?690.47(D) needs to be immediately removed from the Code. It is the only Code rule I am aware of that was added to the Code that makes an installation unsafe.?

The safety problem, as Holt sees it, is that the 2014 version of Section 690.47(D) references Section 250.54, ?Auxiliary Grounding Electrodes,? meaning that system integrators do not need to incorporate the required auxiliary electrode into the premises? grounding-electrode system. As a result, in the event of a lightning strike there could be a difference in potential, or voltage, between an auxiliary electrode and the grounding-electrode system. If that occurred, the difference in potential would induce current in the EGC path. Not only is equipment in this path at risk of damage from lightning-induced surges, but also people could be exposed to a shock hazard, either due to direct contact with an inadvertently energized circuit component or due to a side flash, which occurs when lightning jumps from one object to another.

Brooks concurs with Holt?s assessment: ?If the AHJ requires an additional electrode on a building with an existing electrode, then you should bond the new electrode to the existing electrode following the requirements of Section 250.53. You should make this bond at ground level, not over the top of the building. Making the bond any place other than ground level is asking for lightning damage.?

Brooks continues: ?My basic interpretation is that all buildings with an existing electrode do not require this additional auxiliary electrode because of Exception 2. The building electrode applies to the whole building. So regardless of the physical placement of a ground rod, there is no place on a structure with an electrode that can be farther than 6 feet from the premises? wiring electrode. An uncontroversial example of this is an Ufer ground that is attached to reinforcing steel in the concrete. A reasonable person would agree that the whole slab is part of the grounding system.?
 