Need some feedback on this one...
Client wants to put up to six welding receptacles (480V, 3Ph, 40A each) on a single, 60A three-pole circuit breaker from a distribution panelboard located in the piperack - not far from receptacles. The arc-welders to be utilized have not been defined; and no one knows if they'll l have an integral disconnecting means or not. Plus, the welding recept's do NOT have an integral disconnecting means - they are simply daisy-chained together (in parallel of course) without any additional overcurrent protection or disconnecting means.
Are there any circumstances where this would be allowed?
Client wants to put up to six welding receptacles (480V, 3Ph, 40A each) on a single, 60A three-pole circuit breaker from a distribution panelboard located in the piperack - not far from receptacles. The arc-welders to be utilized have not been defined; and no one knows if they'll l have an integral disconnecting means or not. Plus, the welding recept's do NOT have an integral disconnecting means - they are simply daisy-chained together (in parallel of course) without any additional overcurrent protection or disconnecting means.
Are there any circumstances where this would be allowed?