zoltrix717
Member
It was mentioned in an earlier post the this particluar consumer service had 200A coming in and divided into 6 meter bases with 100A main breaker panels to each one. I'm wondering if that's acceptable, and if so, how does that calculate. Here is Canada, the rule for derating this service is like this.. "100 % of the unit with the heaviest load; plus 65% of the next 2 units; plus 40% of the next 2 units; plus 25% of the next 15 units; plus 10% of the remaining units "