Please explain the proper way of grounding and bonding a system consisting of a 480V Delta utility service and a 480/277V Wye connected generator. The service (phase) conductors from the utility company will terminate at a service entrance panel rated at 400A where the system ground will be established, i.e. water line, building steel, ground rod, etc. The phase conductors and equipment ground will extend to a 3-pole ATS. On the generator side of the ATS, I'm interested in knowing if I should run the neutral and equipment ground from the generator and connect them together at the ATS or tie the neutral and ground together at the generator and simply bring the phase conductors and equipment ground to the ATS. In the latter scenario, if I sized the equipment ground conductor from the generator to the ATS as a main bonding jumper would that suffice to carry the fault current? Like a transformer, I realize the neutral and ground must be connected together at the source of a separately derived system or first disconnecting means. Would that be the generator, ATS, or emergency panelboard? My intent is for the building system ground to be shared with the generator ground and thus the generator would not be a separately derived system. I realize that a low impedance fault current path back to the generator must be present to trip the overcurrent device in the event that a phase to ground fault occurs when the generator is in operation. Yes, I know, a lot of questions with few answers.