bobhudon

Member
In 380VAC, 5-wire systems single phase 220VAC is obtained between any 380VAC leg and the neutral leg. My question is does the neutral leg require a fuse?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: 380VAC, 5-Wire Power

That is a wye system just like 277/480Y and should be treated the same. The neutral is required to be a grounded conductor and fuses are not permitted in grounded conductors. See 250.20(B)(2) and 240.22.
Don
 