3 phase voltage drop

Status
Not open for further replies.

Michael D

Member
Can anyone refresh me on how to calculate voltage drop with this scenerio: 480 volts 3 phase, 400 amp motor load, 800 feet, 600 mcm ran open air in an underground rock quarry?
 

Smart $

Esteemed Member
Location
Ohio
All things being equal--load, distance of run, size and type of conductors, etc.--what is the difference in voltage drop between the two wiring methods depicted below as realized by each load?

VD.gif
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Smart $ said:
All things being equal--load, distance of run, size and type of conductors, etc.--what is the difference in voltage drop between the two wiring methods depicted below as realized by each load?

VD.gif
I'd have to say 2:1, with the shared-neutral scheme being the 1 (with all phases balanced, of course).

The same applies to 240/120v single-phase circuits.
 
Last edited:

Smart $

Esteemed Member
Location
Ohio
Larry and Don,

Thanks for the confirmation. I had to check my sanity :D

However, everyone I've ever seen do a VD calc has used one-way distance for L. Why is that?
 