3/4” EMT

Status
Not open for further replies.

Alpo

Member
Location
Triad, North Carolina
Occupation
Electrician
Would there be a problem with attaching 3/4” EMT to the finished side of a Sealtex ceiling (old 1’x1’ tiles) using one or two hole straps and self tapping metal screws or wood screws. Not sure if 1”x4” wood strips were used to support the ceiling or the metal support channels. The straps would be placed at the joints. Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not an issue as long as the straps are screwed into metal or wood and not just the tile.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How long would EMT stay up screwed to the Celotex tile & not furring strips behind it? 😆
If you used toggle bolts and a lot of straps it might stay up. I once bumped a 2x4 surface mounted fluorescent fixture that was toggle bolted to tile. After being bumped it fell to the floor, wasn't up there very long.
 