277V lighting in bathroom

Status
Not open for further replies.

bonding jumper

Senior Member
Are their any provisions, restrictions against doing this? This is a commercial bathroom for an office. The fixtures are to be installed recessed in the ceiling above the sink, and I was wondering because I am new with 277, if there were any provisions. I missed the one that stated that undercounter lighting must be 120 because it is not a certain distance from the floor, so I was just checking if I was missing any other provisions. Thanks in advance.
 

hassaf

Member
Re: 277V lighting in bathroom

We do that all the time in commecial building if there is 277 available. there is no restriction in code against doing that.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Re: 277V lighting in bathroom

Not that its likely to change your design, but you might check 210.6(C).
 

bphgravity

Senior Member
Location
Florida
Re: 277V lighting in bathroom

Originally posted by bonding jumper:
...I missed the one that stated that undercounter lighting must be 120 because it is not a certain distance from the floor....
What do you mean by this? :confused:
 