240 volt lighting

Status
Not open for further replies.

UncleRico

Member
is there anything in the code that says you have to disconnect all ungrounded conductors for controll(not disconnect) of lighting?for example 240 volt hid lighting,can i use a single pole switch or timer or 1 pole of a contactor?
 

tom baker

First Chief Moderator
Staff member
Re: 240 volt lighting

Yes thats fine, and you recognize that there still is voltage with the controller off. Personally I would use a 240 V lighting relay with a 120V control circuit. You can turn off the load and still TS the controls, and 120 V controls are easier to wire and safer.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 240 volt lighting

I agree with Wayne on both of those articles.

[ April 20, 2004, 04:09 AM: Message edited by: iwire ]
 