Does anybody know if a manufacturer makes a
1600A or 2000A 240/120V, 1Phase, 3Wire busway? GE does not seem to make such a product and Eaton has not called back yet, but catalog does not look promising. Siemens guy never calls back, but I am assuming if GE and Eaton don't make it, then Siemens and SquareD probably don't either.

I assume I cannot use a 3 Phase 3 Wire busway because of labeling requirements. Is this a correct assumption?
I figure there will be mixups with switches as well if this solution was used.

I have 6 existing buildings that need to be retrofitted and busway would be a great solution, but the existing buildings are 240V single phase service for the residential loads and 240v 3p 3w service for large motors. If I change to 208V, 3phase, a lot of motors, including a fire pump would need to be replaced. The cost for that may be prohibitive.

Any suggestions?

JJS
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
According to Square D's busway catalog 5600CT9101 page 31:

Systems:​
ac?3?3W, 3?4W, 1?2W, 1?3W. All neutrals are
100% capacity dc?2-pole

 

jjs

Member
Location
Puryear, TN, USA
Thanks,
I also finally got a reply back from GE, now the rep says the factory said it was ok to do this and that the busway is labeled for it.