I have a situation that I would like run by all. I have been asked to look at a feed to a built in wall oven.
The nameplate rating is 4.8kW.
Table 220.55 note 4--- I use the nameplate at 100%
4.8*1000=4800
4800/240=20amp
I would think I would bump up to #10 with 30 amp OCP