208V Boo Boo

Status
Not open for further replies.

ryan_618

Senior Member
Re: 208V Boo Boo

charred.gif
 

dave55

Member
Re: 208V Boo Boo

As you mentioned ronaldrc, on the middle leg, then every third one. I should mention that now I check voltage and polarity of EVERY outlet I install before allowing anyone to use the outlet.

Dave
 

charlie

Senior Member
Location
Indianapolis
Re: 208V Boo Boo

Sparky59, it can not be anything else than a nominal 208 volts. We are not talking about a corner grounded delta but a 120/240 volt, three phase, 4 wire system where the center point of one phase is grounded. In this system, the voltage from the grounded conductor to the higher phase to ground is a nominal 208 volts. :D
 

Ed MacLaren

Senior Member
Re: 208V Boo Boo

The first sketch might help illustrate the system Charlie is referring to.

By the way, where I live, we are required to install separate panels when the supply is 4-wire delta.(bottom sketch)

Ed

4Wdelta2.gif



Trans14.gif


[ November 19, 2004, 08:05 AM: Message edited by: Ed MacLaren ]
 