The code says "The sum of the ratings of all overcurrent devices connected to power production sources shall not exceed the rating of the service." I just encountered a service with a 400A panel with a 400 MCB that is supplied by a 150kVA pole mounted transformer bank, and the city is still under the 2017 NEC.
Without looking at the transformer, some might think that it's a 400A service, but (150kVA) / (480V)((sqrt(3)) = 180.4A. I talked to an engineer for the city, and he just told me "it happens". Be careful out there.