I'm thinking about bidding on wiring a duplex apartment. I'm going to be honest and say that it's been a while since I've done anything residential. I've been strictly commercial/industrial for 17 years. Anyway, I've done a load calc for the units and decided that a 125 amp panel in each unit is the way to go. I've been researching 2 gang meter bases with service disconnects and I came up with this:
It says in the description that the disconnecting means is rated at 125 amps each but the meter bases themselves are rated at 200 amps. I planned on using a IMT conduit for my mast and 4/0-/4/0-2/0 SE cable in the conduit for my service riser to the meters. The service disconnect breakers are rated at 125 amps. Is this even permissible?
It says in the description that the disconnecting means is rated at 125 amps each but the meter bases themselves are rated at 200 amps. I planned on using a IMT conduit for my mast and 4/0-/4/0-2/0 SE cable in the conduit for my service riser to the meters. The service disconnect breakers are rated at 125 amps. Is this even permissible?