1st UFER.

Status
Not open for further replies.

ritelec

Senior Member
Location
Jersey
Hello.

Will need to install ufer ground this week

250.52(3) says bare or zinc galvanized "or other electrically conductive "coated" steel reinforcing bar"

I was planning on attaching a #4 with an approved clamp to the rebar.

Am I to coat that rebar with something?

Thank you
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Not unless you want to.
The way I read the section, bare is OK; zinc coated is OK; other coatings are OK only if they are conductive.
The main point is that plastic or epoxy coated rebar could not be used to make a UFER since there would be no electrical contact to the concrete.
 