Hello Everyone,
I have an issue where I will need to run short lengths (<6 ft) of 1000V insulated wiring for ampacities up to 400A. Typically for UL 1741 listed equipment we were able to use THHN or AWM, since only the 600V insulation was required. Now, I am looking to find a wire that could be used in a manner much like AWM, but UL 1741 does not mention anything about acceptable wiring methods. I need 1000V rated insulation, minimum. I have looked to UL 508A for guidance, but its ampacity table only goes up to 75 degrees C. Frequently terminals of PV equipment are rated to 90 C, and I would like to use the full ampacity afforded by the conductors-- at these ampacities wire is incredibly expensive! I've identified several types of wiring that might fit my purpose, but I was just wondering if any of the users here had encountered an issue like this before. Could you help me out?
The main candidates I have are:
RHW-2 (not sure how the ratings would apply for internal appliance use) - UL category code (CCN) "ZKST"
PV Wire - UL CCN "ZKLA"
Power & Control Cable - as used in NEC 336, UL CCN "QPOR"
Wind Turbine Tray Cable - UL CCN "ZGZN"
Telco, Battery Cable - UL CCN "ZGZN"
A couple questions:
1. Which wire type do you think would be the cheapest?
2. Are there any you think would be inappropriate for this application?
3. Which ampacity tables should I apply for the internal wiring? UL 1741 does not contain this information. NEC 2011 310.15(B)(16) = 3 conductors in a raceway, @ 30 deg C, then derate to 50 C per the expected ambient temp?
4. It seems that the scope of UL1741 intentionally omitted constraints to wire sizing and type, and perhaps if I merely size my wire such that the terminal temperature ratings and wire insulation ratings are not exceeded, then I am in the clear. Would you agree?
I'm thrilled to have found this forum--I hope to contribute, myself--and I greatly appreciate all of your help!
Dave
I have an issue where I will need to run short lengths (<6 ft) of 1000V insulated wiring for ampacities up to 400A. Typically for UL 1741 listed equipment we were able to use THHN or AWM, since only the 600V insulation was required. Now, I am looking to find a wire that could be used in a manner much like AWM, but UL 1741 does not mention anything about acceptable wiring methods. I need 1000V rated insulation, minimum. I have looked to UL 508A for guidance, but its ampacity table only goes up to 75 degrees C. Frequently terminals of PV equipment are rated to 90 C, and I would like to use the full ampacity afforded by the conductors-- at these ampacities wire is incredibly expensive! I've identified several types of wiring that might fit my purpose, but I was just wondering if any of the users here had encountered an issue like this before. Could you help me out?
The main candidates I have are:
RHW-2 (not sure how the ratings would apply for internal appliance use) - UL category code (CCN) "ZKST"
PV Wire - UL CCN "ZKLA"
Power & Control Cable - as used in NEC 336, UL CCN "QPOR"
Wind Turbine Tray Cable - UL CCN "ZGZN"
Telco, Battery Cable - UL CCN "ZGZN"
A couple questions:
1. Which wire type do you think would be the cheapest?
2. Are there any you think would be inappropriate for this application?
3. Which ampacity tables should I apply for the internal wiring? UL 1741 does not contain this information. NEC 2011 310.15(B)(16) = 3 conductors in a raceway, @ 30 deg C, then derate to 50 C per the expected ambient temp?
4. It seems that the scope of UL1741 intentionally omitted constraints to wire sizing and type, and perhaps if I merely size my wire such that the terminal temperature ratings and wire insulation ratings are not exceeded, then I am in the clear. Would you agree?
I'm thrilled to have found this forum--I hope to contribute, myself--and I greatly appreciate all of your help!