100 amp service on barn

Status
Not open for further replies.

1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I'm installing a 100 amp service on a barn, lean-to, and I would like to confirm ampacity of this service.

I see that table 310.15 (B)(6) is for Dwelling Service, feeders etc. calls for #4 THHN. This is not a dwelling as I see it.

So table 310.16 #3 at 75C is 100 amps.

Right or wrong?
 

bphgravity

Senior Member
Location
Florida
Check with your local building department. In some cases, if the barn is built on a residential zone property and for a non-commercial use, it can be treated as such...
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I agree that you can't use Table 310.15(B)(6), as that table is only for use with Single Phase Dwelling Services.

You are correct with using 310.16

Chris
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Bryan,

I don't believe that a barn built in a residential zone qualifys as a Dwelling.

Just my opinion, what do you think?

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
raider1 said:
Bryan,

I don't believe that a barn built in a residential zone qualifys as a Dwelling.

Just my opinion, what do you think?

Chris


I agree. Sounds more like a detached garage than a dwelling. And yes, #3 THHN/THWN at 75 degrees, 100 amps.
 