An 8 foot ground rod is rated at #6 copper. Is a 10 foot ground rod rated higher?
...if a ufer ground is present you are required to use it.
Bonded yes but never as a grounding electrode.I thought metal gas pipe as well.
Technically the code says that you are supposed to have 8' of rod in the ground, so if you leave 6" sticking out, you are not meeting the code. With the 10' rod it's not an issue.
The purpose of a ground rod is not to clear a line to case fault. Ground rods stabilize the voltage and provide protection from lightning or line surges.
My best advice is to "drive two and go home"
However if a ufer ground is present you are required to use it.
An 8 foot ground rod is rated at #6 copper. Is a 10 foot ground rod rated higher?
...My best advice is to "drive two and go home"
The purpose of a ground rod is not to clear a line to case fault. Ground rods stabilize the voltage and provide protection from lightning or line surges.
My best advice is to "drive two and go home"
However if a ufer ground is present you are required to use it.
Why even make an 8 ft ground rod, if it doesn't meet the code? What application would there be, where you would exhaust the entire length of the ground rod just to meet code required embedment?
The upper end of the electrode shall be flush with or below ground level unless the above-ground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10.
If you "drive two and go home", what electrical specs will that cover you for?
Certainly there has got to be a time when you exceed the capacity of your default two ground rods embedded 8 ft at 6 ft separation.
Well you can drive it all the way in and then use a clamp approved for burial, but I don't see that very often. I do agree with your question about why they make an 8 footer.Why even make an 8 ft ground rod, if it doesn't meet the code? What application would there be, where you would exhaust the entire length of the ground rod just to meet code required embedment?
And, in a physical sense, nothing special happens at 96th inch of embedment, that would make 95 inches of embedment significantly insufficient. There's gotta be a continuous function here, relating embedment depth to the required performance as a grounding electrode.
And, in a physical sense, nothing special happens at 96th inch of embedment, that would make 95 inches of embedment significantly insufficient.
Certainly job specs can require more than 'two and go home' but the NEC never requires more than that.
What capacity do you feel is being exceeded and how is it calculated?
I'm thinking high amperage services, like 4000A. Or maybe high fault currents, or high voltages. It might also relate to the soil properties, instead of the service electrical specs.
I'm not familiar with what property of a service defines the required amount of Earth bonding, but I would like to know how to anticipate "uncharted territory" for which "two and go home" will not be enough. It very well could be, that this is an unrealistic situation to expect.