I know this has been discussed here but I am talking myself in circles whether these are legal or not. I am used to making taps for a relatively large solar backed connection (greater than 60amps) on the load side of the first means of disconnect.
In this particular case it would be easier to connect on the line-side of a 200 amp disconnect, inside the disconnect enclosure.
Is this legal? I would be tapping #4 copper onto 4/0 al on the inside, so they would have no shutoff or until the 80amp PV disco downstream.
I am pretty sure people do this I am just unclear how its justified. Thanks