jmbs
Member
- Location
- marion nc usa
Is it acceptable to power a swimming pool sub-panel with a portable generator and interlock device?
Should the generator be bonded or not, and have its own ground??With the interlock, it’s only switching the hots, so all of the bonding and grounding should still be intact. So shouldn’t be any different than the utility providing the voltage.
If the generator has it's neutral bonded it is a separately derived setup and you must also switch the neutral with your transfer equipment.Should the generator be bonded or not, and have its own ground??