Grouch1980
Senior Member
- Location
- New York, NY
Hi all,
I read articles and literature on current limiting devices and series rated combinations. just a couple of questions as I'm putting some of the pieces together:
1) I understand you can't use current limiting fuses to protect a downstream panel (directly on the load side of the fuses) with modern molded case circuit breakers due to dynamic impedance of the breakers affecting the operation of the current limiting fuses. That being said, if you do try to accomplish this, then the CL fuses and downstream circuit breakers HAVE to be a series rated combination that way the CL fuses operate as intended?
2) If you place CL fuses in a disc. switch, and it feeds a breaker panel, but the panel is not directly on the load side of the disc. switch... there's an ATS switch in between the disc. switch and breaker panel, or the disc. switch feeds a bus duct which then feeds the breaker panel... do these CL fuses and the breakers in the panel have to be series rated? or does series rated only apply if the breakers are directly on the load side of the fuses with nothing else in between?
Thanks!
I read articles and literature on current limiting devices and series rated combinations. just a couple of questions as I'm putting some of the pieces together:
1) I understand you can't use current limiting fuses to protect a downstream panel (directly on the load side of the fuses) with modern molded case circuit breakers due to dynamic impedance of the breakers affecting the operation of the current limiting fuses. That being said, if you do try to accomplish this, then the CL fuses and downstream circuit breakers HAVE to be a series rated combination that way the CL fuses operate as intended?
2) If you place CL fuses in a disc. switch, and it feeds a breaker panel, but the panel is not directly on the load side of the disc. switch... there's an ATS switch in between the disc. switch and breaker panel, or the disc. switch feeds a bus duct which then feeds the breaker panel... do these CL fuses and the breakers in the panel have to be series rated? or does series rated only apply if the breakers are directly on the load side of the fuses with nothing else in between?
Thanks!