How many 90 are allowed in a liquid tight flex ???

Status
Not open for further replies.

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I think As long as you support the flex properly

you can have more than 360' on a run

I was shooting from the hip in my earlier post, I should have opened the code book and I would have said 356.26.

Roger
 

kwired

Electron manager
Location
NE Nebraska
Regardless of the number of pull points you install the answer stays the same, four.
May depend on what you call a "run", you can only have up to 360 degrees of bend between each pull point. You can pull straight through a box or "C" conduit fitting if you wish and have more then 360 degrees in the entire "pull".
 