EdgarC
Member
- Location
- Fontana, CA
How many 90 are allowed in a liquid tight flex ???
I think As long as you support the flex properly
you can have more than 360' on a run
I think As long as you support the flex properly
you can have more than 360' on a run
How many "pull points" do you want to install?How many 90 are allowed in a liquid tight flex ???
How many "pull points" do you want to install?
May depend on what you call a "run", you can only have up to 360 degrees of bend between each pull point. You can pull straight through a box or "C" conduit fitting if you wish and have more then 360 degrees in the entire "pull".Regardless of the number of pull points you install the answer stays the same, four.
May depend on what you call a "run", .
Nope, it does not depend on what we call it.
Its what the OP and the NEC call it.