Ohming

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
more details of what you are trying to accomplish and how you are doing it are necessary. If you are testing with loads still connected especially line to grounded conductor (neutral) loads, I am not surprised at all. You will read whatever resistance is in those loads through the load, then back on the grounded conductor (neutral) back to where that grounded conductor is bonded to the equipment grounding conductor and back through the equipment grounding conductor to your second meter test lead.

If you are searching for faults you have to disconnect paths that are intended current paths so you are only testing for unintended paths that may be there.
 

jcassity

Senior Member
Location
24941
im assuming he has everything unplugged from *ALL* outlets and the fault he describes exists now.

id think he would be tripping breakers as well
 

kwired

Electron manager
Location
NE Nebraska
im assuming he has everything unplugged from *ALL* outlets and the fault he describes exists now.

id think he would be tripping breakers as well

Like I said, we need more information. We don't know what is being tested, whether it is energized, or for that matter exactly what testing methods are employed.

Generally resistance testing is going to involve isolating the item being tested so you don't get readings from something external from what is being tested, if little or no isolation has been done who knows what paths are showing up in his results that may not really be any problem.

Most any grounded system that has equipment operating from the grounded conductor will require isolation from the grounded/grounding bond point for such testing at the very least.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
What is the source?
If the outlets (receptacles?) are fed from a local transformer then interrupting the primary will remove voltage but leave a wire connection through the secondary from hot to neutral. (Assuming single phase or wye.)


Tapatalk...
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
I have a commercial client who's outlets all ohm out to ground, regardless of where you are in the facility. Any help?

Welcome to the forum.

I think it would help if you defined 'ohm out to ground'. Does that mean you are using a DVOM and seeing zero ohms from a conductor to the earth?

Or are you seeing some value, say 100 ohms from a conductor to the earth?

Or are you measuring from a conductor to the grounding conductor in a receptacle?

Or something maybe totally different?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I have a commercial client who's outlets all ohm out to ground, regardless of where you are in the facility. Any help?
Thanks for the feedback. All loads are energized, this is a manufacturing facility 24x7.

These two statements taken together confuse me more than enlighten me. You have not explained what you mean by "ohmed to ground", now you say they are energized. You aren't trying to read ohms on a hot circuit are you? :eek:hmy:
 

kwired

Electron manager
Location
NE Nebraska
exactly what two points did you connect meter leads to when doing your testing? and why did you connect to those points?

Typically a ground fault on an ungrounded conductor doesn't need to use an ohmmeter for initial indication there is a problem, the overcurrent device(s) will be first thing to indicate the problem.
 