Two individual single-pole breakers, without handle tie, ever allowed ?
I am on the 2008 Code cycle. Though the language of the main Code text of 210.4 may not be 100% bullet proof, it would be easy to conclude from 210.4 Code text combined with the related Handbook commentary that if one uses individual single-pole breakers on a multiwire circuit (e.g., L-L 240, L-N 120) then one is "mandated" to have identified handle ties on the breakers.
However, 240.15(B)(1) would seem to throw ambiguity into the situation:, quote:
240.15 Ungrounded Conductors.
(B) Circuit Breaker as Overcurrent Device. Circuit breakers shall open all ungrounded conductors of the circuit both manually and automatically unless otherwise permitted in 240.15(B)(1), (B)(2), and (B)(3).
(1) Multiwire Branch Circuit. Except where limited by 210.4(B), individual single-pole circuit breakers, with or without identified handle ties, shall be permitted as the protection for each ungrounded conductor of multiwire branch circuits that serve only single-phase line-to-neutral loads. ( my underline added ).
= = = =
Looking for some solid ground on this subject...so by 2008 Code would you say there is ever any situation where individual single pole breakers, without handle times, would be code compliant? If so, by what Code section ?
= = = =
Would you interprent any part of 210.4 to say that the only complaint breakers for a multiwire circuit would be either double pole or single poles with handle tie ( therefore prohibiting use of two individual single-pole breakers without handle ties ) ?
If so, what part of 210.4 ?
Thanks, ToolHound
( P.S. -- I would hope always just to use double pole breaker, or handle tie, and thereby circumvent any potential danger and any issues about single-pole breakers and compliance. But, just for purposes of knowing the intended meaning and parameters of the Code, 2008, I dare ask these questions herein. )
I am on the 2008 Code cycle. Though the language of the main Code text of 210.4 may not be 100% bullet proof, it would be easy to conclude from 210.4 Code text combined with the related Handbook commentary that if one uses individual single-pole breakers on a multiwire circuit (e.g., L-L 240, L-N 120) then one is "mandated" to have identified handle ties on the breakers.
However, 240.15(B)(1) would seem to throw ambiguity into the situation:, quote:
240.15 Ungrounded Conductors.
(B) Circuit Breaker as Overcurrent Device. Circuit breakers shall open all ungrounded conductors of the circuit both manually and automatically unless otherwise permitted in 240.15(B)(1), (B)(2), and (B)(3).
(1) Multiwire Branch Circuit. Except where limited by 210.4(B), individual single-pole circuit breakers, with or without identified handle ties, shall be permitted as the protection for each ungrounded conductor of multiwire branch circuits that serve only single-phase line-to-neutral loads. ( my underline added ).
= = = =
Looking for some solid ground on this subject...so by 2008 Code would you say there is ever any situation where individual single pole breakers, without handle times, would be code compliant? If so, by what Code section ?
= = = =
Would you interprent any part of 210.4 to say that the only complaint breakers for a multiwire circuit would be either double pole or single poles with handle tie ( therefore prohibiting use of two individual single-pole breakers without handle ties ) ?
If so, what part of 210.4 ?
Thanks, ToolHound
( P.S. -- I would hope always just to use double pole breaker, or handle tie, and thereby circumvent any potential danger and any issues about single-pole breakers and compliance. But, just for purposes of knowing the intended meaning and parameters of the Code, 2008, I dare ask these questions herein. )