does GB count as a lock nut

Status
Not open for further replies.

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
Sometimes the threads of a fitting are not long enough to accommodate the lock nut and the grounding bushing. In this case is it allowed to leave out the lock nut and just install the grounding bushing? Basically the GB acts like a lock nut and as a grounding bushing.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would say no. The fitting is listed and tested with a locknut. A metal bushing and one locknut on RMC would be a different story.
 

guschash

Senior Member
Location
Ohio
Bushing that's metal, we used them all in the Industial plant I working. Had to it was so hot plastic would melt.
 

480sparky

Senior Member
Location
Iowegia
What is a metal bushing?

2012629155865.jpg
 

iwire

Moderator
Staff member
Location
Massachusetts
I only have a second but somewhere there is a code section that says that bushing made solely of insulating material shall not be used in place of a locknut' That leads me to believe a metal bushing could be used in place of a locknut and I see it often in old buildings around Boston.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
I only have a second but somewhere there is a code section that says that bushing made solely of insulating material shall not be used in place of a locknut' That leads me to believe a metal bushing could be used in place of a locknut and I see it often in old buildings around Boston.

A grounding bushing is not made of an insulation material. But is it a code issue or a UL listing issue?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I only have a second but somewhere there is a code section that says that bushing made solely of insulating material shall not be used in place of a locknut' That leads me to believe a metal bushing could be used in place of a locknut and I see it often in old buildings around Boston.

I agree, very common in older buildings. Once your conductors get to #4 or larger the bushing can no longer be solely made of metal as it's required to be insulating.
 

jusme123

Senior Member
Location
NY
Occupation
JW
I only have a second but somewhere there is a code section that says that bushing made solely of insulating material shall not be used in place of a locknut' That leads me to believe a metal bushing could be used in place of a locknut and I see it often in old buildings around Boston.

300.4(G)
 

guschash

Senior Member
Location
Ohio
We had to use all fiberglass conductors, the temperatures ran from 2000 down to 185 when the glass was be cut. So hot we could work only 10 to 15 minutes in the heat. We had to use porcelain connectors,plastic would melt.
 