Nema 9 box

Status
Not open for further replies.

ravenjoe

Member
I have a Class II Div 2 group F installation. Do my penetrations have to be threaded bosses for conduit. Am I interpreting 502.10(B) correctly? Drill and tap or pre-tapped from factory?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Class II, Division 2 enclosures are not required to have threaded hubs or bosses. Often you find boxes that are dual listed for NEMA 7 and NEMA 9 and those boxes will have threaded connections.
 