What if I want to bend a kick at say 30 degrees, to reach a coupling 17" away. Would I just mark the pipe at 17" and put it at the front of the shoe and bend it till it reaches 30 degrees? Thank you for your help.
The pipe will lengthen, so deduct would count. You will end up cutting a short piece off.
So say a 90 degree bend the shoe say's 5" deduct. So would a 45 degree be a 2.5" deduct?
What I think your asking is there a way to determine where to start your bends, no.* A multiplier of 60^ is 1.2 and is your smallest multiplier when bending, and in fact is not a deduction.
*Well you can approximate once you determine your multiplier, but it sounds like your going to have to cut off the existing run, IE your to close...
Your multiplier for 30^ is 2: thus 2x 17" = 34". This will get you past object with no distance between what your trying to get by, your flush and touching object your trying to get past.
Your bending an offset! The distance your traveling is measured by determining the depth that the conduit needs to pass by your 17", then you use a multiplier of the desired angle you want to bend.
I'd add the distance of a mineral-lac (stand-off)+ .1/2" if you need to, or add the depth of insulation if required.
Mark the sum on two place on conduit and bend on the arrow to the multiplier, do not reverse the shoe, just turn it over...
You need to buy an Ugly Book
Zappy, if you measure from the end of your conduit to the wall and the measurement is 65", you need a 65" (90 degree bend) to go up the wall. take a full length of pipe and place it on the floor, measure 65" and place a mark on the pipe, THAN take the 5" deduct that is stamped on the bender and subtract that from the 65" you marked on the conduit on the floor. Now you should have a mark on the pipe at 60". Now take your bender and face the end of the pipe you started measuring from and place the arrow (stamped on the bender) on the 60" mark and bend until it is a 90 degree bend. The deduct 5" is for 90 degree bends only for that specific bender and conduit size
There is no deduct for a kick. You have to think about shrink, but it is a different concept. The notch on your bender is the center of a kick.
Generally, you can ignore thinking about shrink, because you have the option to stop running the portion of the conduit you're working on, begin at the other end to meet yourself in the middle and avoid the math.
Look for the shrink values on your bender. 30 degree kicks are 3/16" of shrink for every inch of offset. A kick is technically an offset too.
Zappy, quit saying you are sorry. We all mis-post a reply here and there.
You are polite enough (this a compliment)-you need not apologize.
It is always cool to see you here. Where in CA are you?
Thank you George. You lost me on the second paragraph. Don't you mean 1/4" of shrink for a 30 degree bend? I thought because your bending at a radius, there would be a gain, but your saying it's shrink. I going to experiment this weekend. Thanks George.
For every bend, you gain a little bit of distance. We typically measure straight-line run distance. Every bend shortcuts that distance with a curve.I don't see how you gain pipe by bending it, that doesn't make sense. Think about a 10' stick of pipe. Bend it a little, it will lot be as long, measured along the same axis.
On paper, conduit per degree of bend is constant. Varies a little in actual bending.Zappy, I want to say yes - if a 90 bend is 5" then a 45 should be 2.5", but I am leery. The math seems right, but benders vary and I do not want to commit to it. I have my benders handy but no conduit to test.