XHHN - XHWN-2

Status
Not open for further replies.

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Greetings all the 2017 Code was changed to add XHHN, XHWN, XHWN-2
T 310.104(A)
I assume this is a XHH with an outer Nylon jacket?
I am not familiar with this marking, does anyone use this stuff?
Thanks in advance.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Greetings all the 2017 Code was changed to add XHHN, XHWN, XHWN-2
T 310.104(A)
I assume this is a XHH with an outer Nylon jacket?
I am not familiar with this marking, does anyone use this stuff?
Thanks in advance.
N always means Nylon jacketed for resistance to oil and gas, so I'd say you got it.
X = XLPE insulation material
H = High (heat)
W = Water Resistant
N = Nylon jacketed (in all other wire insulation definitions)
-2 = 90C wet or dry (without the -2 it is 75C wet, 90C dry)

I have a copy of UL-44 (for this type of cable) and it isn't in there, but mine is dated 2002 and the latest edition is 2015, so they may have added it.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
...
I have a copy of UL-44 (for this type of cable) and it isn't in there, but mine is dated 2002 and the latest edition is 2015, so they may have added it.
It was added to Table 310.104(A) for the 2017 code. I have never seen it.
 

tom baker

First Chief Moderator
Staff member
Our preferred wire for street lighting is XHHW-2. Holds up far better than THHN/W, which has a very thin insulation and easy to damage, ok inside. Underground I have seen THHN/W fail.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Our preferred wire for street lighting is XHHW-2. Holds up far better than THHN/W, which has a very thin insulation and easy to damage, ok inside. Underground I have seen THHN/W fail.
Yes, I specify XHHW for all underground as well as for VFD applications.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Our preferred wire for street lighting is XHHW-2. Holds up far better than THHN/W, which has a very thin insulation and easy to damage, ok inside. Underground I have seen THHN/W fail.

Yes, I specify XHHW for all underground as well as for VFD applications.

I do as well. I find supply houses don't stock allot of XHHW-2 copper.
I get loads of complaints that its more difficult to strip the smaller sizes like 10 XHHW-2 copper.

But none of you have seen XHHN?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I do as well. I find supply houses don't stock allot of XHHW-2 copper.
I get loads of complaints that its more difficult to strip the smaller sizes like 10 XHHW-2 copper.

But none of you have seen XHHN?
It is more difficult to strip in the smaller sizes and the OD is substantially greater in the smaller sizes than THWN.

I have never seen the nylon jacketed version. It does not even appear in Chapter 9, Table 5.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Well its almost been two years since I posted this.
Has anyone seen XHHN yet? Not XHHW we all have seen that. XHHN as in November.
Its so strange a product that does not exist got added to the code.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Bump..
Mods please dont lock this thread no matter how old it gets until someone posts a pic of XHHN.
Its now nearing three years since I posted this, still no sign of XHHN.
(Not XHHW we all have seen that. XHHN as in November)
Why is a product that does not exist in the code?
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Interesting, this designation appears in none of the other 310 tables, nor in the chapter 9 tables. So even "if" we could find it, there is no guidance as to application or amperage/temperature. I wonder if Southwire is developing a product like their SimPull that has a slick outer coating eliminating (per mfg specs) the need for pulling lube. According to table 310.104(A) the designation differs from the typical xhhw-2 in that it has an outer covering of a nylon jacket.
 

Carultch

Senior Member
Location
Massachusetts
Bump..
Mods please dont lock this thread no matter how old it gets until someone posts a pic of XHHN.
Its now nearing three years since I posted this, still no sign of XHHN.
(Not XHHW we all have seen that. XHHN as in November)
Why is a product that does not exist in the code?

Maybe because there are proposals from manufacturers to make such a wire, and the code article is based on the product's proposed spec's, so that a testing standard can be developed for it.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Why is it so important to know this? xhhn was allowed by the nec but was it necessary. The manufacturers obviously don't see a need for it. Someone probably thought it was a good idea..... obviously it wasn't.
 