xfrmr lug kits

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Looks like that kit may work. The four larger lugs for the secondary and the smaller lugs for the primary and grounding.
 

MD Automation

Senior Member
Location
Maryland
Occupation
Engineer
Fyi… most of the 3 phase transformers I have purchased in the last few years come with some type of grounding block already installed.

That being said, they tend to sometimes be comically large or small. I am talking about xfrmr sizes of 20 – 30 KVA and you either have something really tiny like this…

1L7A9223_1.JPG



Or something super oversized like this…

1L7A9228_1.JPG


I know the large one is rated for 350 Kcmil - #12 AWG, that’s quite a range! I say this mostly in jest, but I think I had trouble fitting a stranded #10 in the small one and keeping a #10 in the big one.

Anyway.. just pointing out you might not need to purchase individual (grounding) lugs for your primary and secondary conductors if your unit comes with a grounding block already installed.
 