Will a 5-30R or 6-30R fit in a 3 X 2 X 3-1/2 device box?

Status
Not open for further replies.
Has anyone mounted a 5-30R or 6-30R power receptacle in a 3 X 2 X 3-1/2 device box? They make single gang cutouts for this but it seams tight to me.
 

iwire

Moderator
Staff member
Location
Massachusetts
I think a better question is will the conductors fit?

I would use a 4-11/16" deep box with a single gang plaster ring if I had to have a single gang look.

What is the reason for the small box?
 