Welder Branch Circuit

Status
Not open for further replies.

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
OK.....Here is my stumper for today....

The maximun overcurrent protection device rating for a #10THHN used for an arc welder branch circuit is...

A. 30a
B. 40a
C. 50a
D. 70a

My thinking is it is 80a based on 630.12 (B). #10 THHN is rated at 40a from 310.16 and I just went to 200% of that. But 80a is not a choice so I guess I'd go for answer D. Any takers?
 

jtester

Senior Member
Location
Las Cruces N.M.
I find the correct answer in your list of options. How did you determine that #10 is good for 40 amps? Did you consider the temperature rating of the OCPD it is attached to?

Jim T
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
My Bad.....I forgot to use the 75C column. I now see that 70a is the correct choice. Now I'm wondering about motors and 430.22 and 430.52. I assume we apply the 75C column for motor brach circuit ampacity too, right?
 

mario

Senior Member
Location
Alaska
:?: .. where did you get the 200% from ? I'm assumming it has to do with "Duty Cycle" ... forgive my ignorance ... :oops:
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
The 200% came out of 630.12 (B). Nobody in this trade is ignorant.....it is by asking questions we all learn. Believe me, I have way more questions than answers...
 