Does anyone know if a Waste Oil recycle storage tank and Oil Filter Crusher , located inside of a Shipping Container , where a person walks in and dumps used oil into a tank would be considered a Classified Location ? Studied NFPA , NEC understand gasoline and other flammables , can't find Oil , other than it has a higher flash point as a combustible not sure about its classification or wiring methods . Help would be greatly appreciated . Thanks !
 

kwired

Electron manager
Location
NE Nebraska
It does not give off easily ignitable gases under normal temp and pressure conditions like gasoline does, those gases are what causes the classification.
 

FWD

Member
Does anyone know if a Waste Oil recycle storage tank and Oil Filter Crusher , located inside of a Shipping Container , where a person walks in and dumps used oil into a tank would be considered a Classified Location ? Studied NFPA , NEC understand gasoline and other flammables , can't find Oil , other than it has a higher flash point as a combustible not sure about its classification or wiring methods . Help would be greatly appreciated . Thanks !

Thanks , getting mixed info on NFPA classification weather its 111b flash point 200 F or above same as cooking oil , or class 11 101 F - 140 F same as diesel . Do you happen to know which one ?
 
Last edited:

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Thanks , getting mixed info on NFPA classification weather its 111b flash point 200 F or above same as cooking oil , or class 11 101 F - 140 F same as diesel . Do you happen to know which one ?
In your particular case it doesn't matter whether it is Class II or Class IIIB. See NFPA 497, Section 4.2.7. If you still have a concern, consult with a relevant MSDS.
 