Voltage drop conductor size

Status
Not open for further replies.

JJWalecka

Senior Member
Location
New England
Hypothetical....#12 from panel to JB.....then #10 from JB to load.....seems ass backwards but would it still assist with voltage drop?

Ideally it would be #10 then #12.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
It makes no difference. It is not unusual to have, say, a 20 amp circuit with way oversized conductor in the middle and #12 at each end.
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
As has been mentioned, it makes no difference which order you have the two different conductor sizes with a single load.
Now if you have multiple runs to loads that branch out from the JB, then it's more efficient to put the larger conductor before the JB because it will have the highest current.
 

retirede

Senior Member
Location
Illinois
It depends on where the j-box is located. You probably want the big wire on the long side.

It wouldn’t make sense to run 200’ of 12 to the j-box and 20’ of 10 on to the load.
 