Have a charger thats rated 48A @240V
Mfgrs install states 60A CB or 60 fuse. Cu conductors.
I thought I recalled a thread here that said #6 Cu NM cable was non code compliant.
55A. Next size standard OCPD 60 A. Not supplying multioutlet receptacle branch circuits.
Thank you
Where do you transition to Cu per Mfg specs?I have been using aluminum SER for chargers recently.
The ones I have done plug in, so at the receptacle.Where do you transition to Cu per Mfg specs?