use a #12 ground in a conduit with #10's ?

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Or I could even downsize my wire to my original #10 if I just install 20 amp, 240 v subpanel. (customer wants two circuits,, one for gate opener, one for outlets for lighting) Am I off base, or crazy ?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
If you're running two circuits to the same building, you would have to run a 240V circuit to a subpanel anyway. Unless the circuit is a MWBC, you can't run more that one circuit to a separate building.
The 240V would definitely help with VD as well
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
It's two circuits to the end of a driveway, by the county road.
If the big load is the motorized gate, look for one that works with 240 input. Your %VD improves by a factor of 4. (120V, 20A sounds like a pretty big motor for a gate.) Your VD should be based on the actual load, not the OCPD size.
Or look for a DC operated gate with a battery that can be recharged at a much lower power consumption.
 