I am running URD approximate 250 feet direct bury. feeding 200 amp service on house. what size Al URD do I need?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I am running URD approximate 250 feet direct bury. feeding 200 amp service on house. what size Al URD do I need?
Are you asking about voltage drop compensation? What is your current? Using the Southwire app with 150 amps I come up with 300 kcmil Al. Using the section Ron posted the minimum size would be #4/0.
 