I am currently designing a multi-building school, with a single main switchboard, and feeder panels in the outlying buildings. There is a counterpoise ring around each building, and each ring is bonded together. The system is 480Y277 volts.
Citing Article 225.36, the plans reviewer has required that I make these feeder panels "suitable for use as service equipment". This brings up a concern for me in that I believe there will be a bonding strap between the neutral bus and ground bus in the ULSE panels. There would therefore be a parallel path for neutral current flow back to the main switchboard, a situation clearly prohibited by Article 250.32(B)(1).
Can anyone provide some clarification? Should I have the installer remove the bonding strap in the panels, and if so, wouldn't this invalidate UL's listing? Should I simply not pull in an EGC with the feeder?
Thanks in advance for your help with this problem.
Citing Article 225.36, the plans reviewer has required that I make these feeder panels "suitable for use as service equipment". This brings up a concern for me in that I believe there will be a bonding strap between the neutral bus and ground bus in the ULSE panels. There would therefore be a parallel path for neutral current flow back to the main switchboard, a situation clearly prohibited by Article 250.32(B)(1).