UL listing for an old panel enclosure used as a junction box

Status
Not open for further replies.
Location
Orange County Ca
Occupation
Electrical contractor
I am installing a new 200 amp panel and the homeowner did not want any stucco repair done. I mounted the new panel adjacent to the existing as shown. I was going to come out the side of the new panel with 1-1/4" sealtite and connect to the front of the existing panel to feed all the existing circuits. The inspector wrote me up saying" Provide information for UL listing compliance of bored hole is board hole into front of old panel." Is this OK as I have seen it before. I know the sealtite fitting is rated and the cover is rated, but is it still rated when I attach the fitting. There are 2 other covers that could be opened for access to the interior and I was planning on screwing the bottom left cover on place. I appreciate your help on this one. Having issued with the photos

https://linksharing.samsungcloud.com/g7eAl9yYQ2Vm.
https://m.facebook.com/photos/viewer/?photoset_token=pcb.10222672050101293&photo=10222672049301&profileid=1574525909&source=49&refid=17&_ft_=mf_story_key.10222672050101293%3Atop_level_post_id.10222672050101293%3Atl_objid.10222672050101293%3Acontent_owner_id_new.1574525909%3Athrowback_story_fbid.10222672050101293%3Aphoto_attachments_list.%5B10222672048941264%2C10222672049301273%2C10222672049661282%5D%3Astory_location.4%3Astory_attachment_style.album%3Athid.1574525909%3A306061129499414%3A2%3A0%3A1633071599%3A8346249888263814659%3A%3A%3Acta_types.1&__tn__=EH-R
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
The inspector wrote me up saying" Provide information for UL listing compliance of bored hole is board hole into front of old panel." Is this OK as I have seen it before.
So this is an overhead service and your just refeeding branch circuits and gutting the old meter / main?

If your converting a article 312 'cutout box' to a article 314 junction box, 314.15 applies.
Its the AHJ's call , I'd tell the customer we need to notch the stucco.
Here is your photo:
 

Attachments

  • removable_cover.jpeg
    removable_cover.jpeg
    81.4 KB · Views: 27
Location
Orange County Ca
Occupation
Electrical contractor
Knotch the stucco to come into the bottom of the junction box?
So this is an overhead service and your just refeeding branch circuits and gutting the old meter / main?

If your converting a article 312 'cutout box' to a article 314 junction box, 314.15 applies.
Its the AHJ's call , I'd tell the customer we need to notch the stucco.
Here is your photo:
Thanks for getting the photo, the other photo didn't make it I guess.
 

ppsh

Member
Location
CA
Occupation
Electrician
Looks like one 1-1/4" entering the old utility compartment? What is your plan for un bonding the neutral bar in the old meter main?
 