Typical feeder installation for trailer/manufactured home

Status
Not open for further replies.

sw_ross

Senior Member
Location
NoDak
With the disconnect switch adjacent to the structure How do you typically install your feeder to the interior panel?
If you show up and the trailer is set up onsite, you can’t trench to the location where the interior panel is located.

previously I’ve dug my feeder until it’s under the trailer then came to surface under trailer and sleeved the feeder under the trailer on the surface of the ground (usually on the plastic vapor barrier) with ENT until I get to the pvc conduit riser where the panel is located and coupled the pvc to the ent.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Locally it's PVC all the way. If the service pole is within 12" of the mobile home we allow the conduit to run above ground directly between, otherwise trench, then up to the frame and fastened to the frame.
 