two pole GFCI
zaid
I know that 2 pole GFCI Circuit Breaker is designed for multiwire brach circuit (that is 3 wire circuit 2 phase and common neutral.) can we install 2p gfci circuit breaker to protect 220V receptacle (two wire circuit)??
jim dungar
Wisconsin
PE (Retired) - Power Systems
Re: two pole GFCI
Yes.
All two pole GFCI breakers I have ever seen are rated for 2 wire and 3 wire circuits.
Note: The line side neutral wire (the white curly one) must always be connected to the panel neutral.
zaid
Re: two pole GFCI
Thank you Tom, my point is if it is possible to use 2 pole GFCI circuit breaker to protect 220V receptacle (phase to phase), not that circuit with a common neutral?
is 2 pole GFCI CB approved for such circuit?
[ June 19, 2003, 07:52 PM: Message edited by: zaid ]