Designer101
Senior Member
- Location
- California
- Occupation
- Solar and ESS Designer
We recently installed solar on line side of ATS using external tap box and city approved the installation , inspected and passed.
Now for the interconnection utility is giving us hard time.
the Generator installed previously was not given permission to operate by POCO. so They advised us to Take responsibility. we did it thinking it would be simple.
The existing system has 22 kw Generac generator but has two ATS switches ( the main lines form generator is spliced into two using Polaris connector)That goes to incoming lugs of each 200A, 200A bus bur at 400A Rated split phase main panel.
and the main safety concern is what i didn't understand, code section also specifies the external ac disconnect for generator does that mean that or something else.
their exact word copied.....
SCE has reviewed your Interconnection Request and has identified the following deficiency or deficiencies:
The ATS manual does not contain the specific terms ""Break before make" or "Open Transition") to confirm the isolated mode of operation.
Please provide the ATS documentation which contains these terms.
As per the modified SLD provided, there is a direct electrical path from the generator to the main service panel which is a safety hazard. Please verify and update., Please let us know why two ATS switches are employed to interconnect the generator in this project as there is only a single generator installed, Please provide a SLD with PE stamp on it.
I have attached SLD and interconnection pics to explain things clearly. Please give me your insights.
Now for the interconnection utility is giving us hard time.
the Generator installed previously was not given permission to operate by POCO. so They advised us to Take responsibility. we did it thinking it would be simple.
The existing system has 22 kw Generac generator but has two ATS switches ( the main lines form generator is spliced into two using Polaris connector)That goes to incoming lugs of each 200A, 200A bus bur at 400A Rated split phase main panel.
and the main safety concern is what i didn't understand, code section also specifies the external ac disconnect for generator does that mean that or something else.
their exact word copied.....
SCE has reviewed your Interconnection Request and has identified the following deficiency or deficiencies:
The ATS manual does not contain the specific terms ""Break before make" or "Open Transition") to confirm the isolated mode of operation.
Please provide the ATS documentation which contains these terms.
As per the modified SLD provided, there is a direct electrical path from the generator to the main service panel which is a safety hazard. Please verify and update., Please let us know why two ATS switches are employed to interconnect the generator in this project as there is only a single generator installed, Please provide a SLD with PE stamp on it.
I have attached SLD and interconnection pics to explain things clearly. Please give me your insights.