hhsting
Senior Member
- Location
- Glen bunie, md, us
I have three phase 50kva transformer 480V delta primary and 208/120V secondary. Please see the transformer link below
www.eaton.com
The secondary panelboard provided is 240/120V single phase.
The designer has brought from the transformer secondary two legs two phase wires and one neutral wire and one equipment grounding conductor to the secondary single phase panelboard. The third leg/phase terminal of the transformer is left open nothing connected. Would this be NEC 2014 code compliant or not?
V48M28T5016 | Eaton General purpose ventilated transformer | Eaton
V48M28T5016 - Eaton General purpose ventilated transformer, Fungus proof, AL windings, DOE 2016, NEMA 2, 220°C, 50 kVA, Floor/wall mnt upright only, 3-phase, PV: 480V delta, SV: 208Y/120, NEMA ST-20, 2 at +2.5%, 4 at -2.5%, 150°C, 50 kVA
The secondary panelboard provided is 240/120V single phase.
The designer has brought from the transformer secondary two legs two phase wires and one neutral wire and one equipment grounding conductor to the secondary single phase panelboard. The third leg/phase terminal of the transformer is left open nothing connected. Would this be NEC 2014 code compliant or not?